[Hai-users] Upgrade RC-100 to RC-1000 (resubmitted with imagesremoved)
Brad
looney2ns at wowway.com
Mon Jan 2 16:33:34 CST 2012
Frank,
I believe if you connect a common wire on terminal 3 of the tstat, and connect it back at the common at the furnace transformer, it will solve the problem.
Look at figure 7 on page 8..
From: Frank Goodyear
Sent: Monday, January 02, 2012 3:31 PM
To: HAI-users at tssi.com
Subject: [Hai-users] Upgrade RC-100 to RC-1000 (resubmitted with imagesremoved)
Having an issue with getting the RC-1000 to work properly. Should be a simple installation but I definitely overlooking something.
I'm changing from a RC-100 thermostat to a RC-1000. The existing RC-100 works just fine.
I have a Carrier single stage heat pump, it uses only one 24 volt transformer.
I remove the RC-100 and installed the RC-1000, connected wire, thermostat lights up, configured the RC-1000 for heat pump, connection to HAI functioning, fan turns on and off manually. BUT when I select heat, the compressor just clicks and doesn't start up.
Since there are only 5 wires, 2 for the 24 volt, 1 for the reversing valve, 1 for the fan, and one for the compressor relay should be a no brainer. The jumper is on for using one 1 24 volt transformer.
I've have checked the settings in the RC-1000 and they are as per instructions for heat pump.
I have links to a photo of the RC-100 base and the RC-1000 base with the wires connected.
www.cobrahouse.com/img/rc-100.jpg www.cobrahouse.com/img/rc-1000.jpg
I switched back to the RC-100 and everything works fine.
Help!
--------------------------------------------------------------------------------
_______________________________________________
HAI-users mailing list
HAI-users at tssi.com
http://romaine.tssi.com/mailman/listinfo/hai-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://romaine.tssi.com/pipermail/hai-users/attachments/20120102/7fd7db9f/attachment.html>
More information about the HAI-users
mailing list