[Hai-users] Re: Any Resolution to HAI Temp Sensors? (Rager, Brent A)

Kenneth McLeod kmcleod at prodigy.net
Tue Apr 5 08:36:04 CDT 2005


Brent, it appears you have installed the new extended range temperature
sensors. but the Omni board is not aware of that.
You need to: (#1) make sure that you have the 2.8 firmware on the Omni, (#2)
Assign the temperature zones to the ER (extended range) type, (#3) Make sure
you have the 2.8 access software if you want to be able to see the zone
through PC access.

HAI temperature sensors are generally quite accurate, but the humidity
sensors have some real issues and can misread by 30% or more on humidity.
Check yours out if you can borrow a sling psychrometer or other humidity
gauge.  Hopefully this issue has been corrected on the newer ER units.

Ken McLeod
Integrated Home Technologies
Eau Claire, WI

>
> Installed a Temp sensor in the attic and a Temp Humidity on a project
> this weekend and both were 42F + over ambient temperature.  Was there
> any fix for this?  The house is only about 90% done with no phone
> service so I can't call in and see if whether the performance improves
> over time.
>
> Brent Rager
>