[Hai-users] RS232 arming bug workaround?
Tony Golden
MrGolden at earthlink.net
Sun Jan 15 08:04:41 CST 2006
I'll email you the latest version of the module, which has an additional
input for enabling this feature. It also has a few other enhancements,
improving overall performance and reliability.
_____
From: hai-users-bounces at tssi.com [mailto:hai-users-bounces at tssi.com] On
Behalf Of Barry Newton
Sent: Saturday, January 14, 2006 10:11 AM
To: hai-users at tssi.com
Subject: RE: [Hai-users] RS232 arming bug workaround?
I'm actually using your Crestron module and it is omnilink after all, my
mistake. I don't see any sort of option for Force Arming in the Omni
configuration -- can you point me to the right place?
_____
From: hai-users-bounces at tssi.com [mailto:hai-users-bounces at tssi.com] On
Behalf Of Tony Golden
Sent: Saturday, January 14, 2006 8:55 AM
To: hai-users at tssi.com
Subject: RE: [Hai-users] RS232 arming bug workaround?
I never use the ProLink (ASCII-based) protocol, but with the *OmniLink*
protocol you are able to arm with zones open, provided Force-Arming is
enabled. That wasn't always the case, because I remember trying it several
years ago and it didn't work. At that time (around 2001, give or take a
year) I called HAI's tech support and was told you couldn't force-arm via
RS-232. However, I've tried it recently and it *does* work.
I don't know when the change was implemented, but I've verified that panels
as old as 2.2 firmware will allow it.
________________________________________
From: hai-users-bounces at tssi.com [mailto:hai-users-bounces at tssi.com] On
Behalf Of Barry Newton
Sent: Friday, January 13, 2006 5:33 PM
To: hai-users at tssi.com
Subject: [Hai-users] RS232 arming bug workaround?
As I understand it, there is a bug whereby you cannot arm an Omni (Pro II)
system via the serial prolink protocol if there are any zones not secured. I
want to replace my keypad at the door with a touchscreen, but this door
leads out through the garage. When I leave I like to arm and then shut the
garage overhead door on the way out, but the garage overhead door is a zone.
So using a touchscreen via RS232 I can't arm and leave. Anyone have ideas
for a workaround?
Thanks, Barry
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://romaine.tssi.com/pipermail/hai-users/attachments/20060115/4b780aea/attachment.htm
More information about the HAI-users
mailing list